2.1 Determine the value of the phase voltage in a delta-connected system if the line voltage is 380 V - NSC Electrical Technology Electronics - Question 2 - 2016 - Paper 1

Question icon

Question 2

2.1-Determine-the-value-of-the-phase-voltage-in-a-delta-connected-system-if-the-line-voltage-is-380-V-NSC Electrical Technology Electronics-Question 2-2016-Paper 1.png

2.1 Determine the value of the phase voltage in a delta-connected system if the line voltage is 380 V. 2.2 Draw a neat, labelled voltage phasor diagram that represe... show full transcript

Worked Solution & Example Answer:2.1 Determine the value of the phase voltage in a delta-connected system if the line voltage is 380 V - NSC Electrical Technology Electronics - Question 2 - 2016 - Paper 1

Step 1

2.1 Determine the value of the phase voltage in a delta-connected system if the line voltage is 380 V.

96%

114 rated

Answer

In a delta-connected system, the phase voltage ( V_{ph}) is equal to the line voltage ( V_L). Therefore, given that the line voltage is 380 V, we have:

Vph=VL=380extVV_{ph} = V_L = 380 ext{ V}

Step 2

2.2 Draw a neat, labelled voltage phasor diagram that represents a three-phase delta-connected system.

99%

104 rated

Answer

The voltage phasor diagram for a three-phase delta-connected system consists of three phasors, each separated by 120 degrees. The three voltages can be labeled as:

  • VL1V_{L1} (Phase R)
  • VL2V_{L2} (Phase Y)
  • VL3V_{L3} (Phase B)

Each phase voltage is represented as:

  1. VL1V_{L1} at 0 degrees
  2. VL2V_{L2} at 120 degrees
  3. VL3V_{L3} at 240 degrees

This configuration illustrates the balanced nature of the system.

Step 3

2.3.1 Current delivered by the alternator at full load

96%

101 rated

Answer

The current delivered by the alternator at full load can be calculated using the formula:

IL=S3VLI_L = \frac{S}{\sqrt{3} V_L}

Substituting the known values:

  • S=20kVA=20×103VAS = 20 kVA = 20 \times 10^3 VA
  • VL=380VV_L = 380 V

We find:

IL=20×1033×38030,39AI_L = \frac{20 \times 10^3}{\sqrt{3} \times 380} \approx 30,39 A

Step 4

2.3.2 Power rating of the alternator

98%

120 rated

Answer

To calculate the power rating of the alternator, the following formula is used:

P=3VLILcosθP = \sqrt{3} V_L I_L \cos \theta

Where:

  • cosθ\cos \theta is the power factor. Given a power factor of 0.87:
P=3×380×30,39×0,8717,4kWP = \sqrt{3} \times 380 \times 30,39 \times 0,87 \approx 17,4 kW

Step 5

2.4 State the function of a kilowatt-hour meter.

97%

117 rated

Answer

The function of a kilowatt-hour (kWh) meter is to measure the amount of energy consumed over time. This device quantifies the electrical energy used by a load in kilowatt-hours, allowing for the billing of electricity by utility companies.

Step 6

2.5 State TWO methods used to improve the power factor of a resistive inductive load.

97%

121 rated

Answer

Two common methods to improve the power factor of a resistive inductive load are:

  1. Adding power factor correction capacitors in parallel with the load.
  2. Using synchronous motors which can be operated under leading power factor conditions to compensate for lagging loads.

Step 7

2.6.1 Calculate the power consumed by the load.

96%

114 rated

Answer

The power consumed by the load can be determined by summing the readings from the two wattmeters:

Ptotal=P1+P2=120W+50W=170WP_{total} = P_1 + P_2 = 120 W + 50 W = 170 W

Step 8

2.6.2 TWO advantages of using the two-wattmeter method when measuring the power of a balanced load.

99%

104 rated

Answer

The advantages of the two-wattmeter method include:

  1. It allows for the measurement of power in both balanced and unbalanced loads.
  2. It can determine the power factor of a balanced load directly, providing valuable information about system efficiency.