2.1 Determine the value of the phase voltage in a delta-connected system if the line voltage is 380 V - NSC Electrical Technology Electronics - Question 2 - 2016 - Paper 1

Question icon

Question 2

2.1-Determine-the-value-of-the-phase-voltage-in-a-delta-connected-system-if-the-line-voltage-is-380-V-NSC Electrical Technology Electronics-Question 2-2016-Paper 1.png

2.1 Determine the value of the phase voltage in a delta-connected system if the line voltage is 380 V. 2.2 Draw a neat, labelled voltage phasor diagram that represe... show full transcript

Worked Solution & Example Answer:2.1 Determine the value of the phase voltage in a delta-connected system if the line voltage is 380 V - NSC Electrical Technology Electronics - Question 2 - 2016 - Paper 1

Step 1

Determine the value of the phase voltage in a delta-connected system if the line voltage is 380 V.

96%

114 rated

Answer

In a delta-connected system, the phase voltage (VphV_{ph}) is equal to the line voltage (VLV_L). Therefore, the phase voltage can be expressed as:

Vph=VL=380extVV_{ph} = V_L = 380 ext{ V}

Thus, the phase voltage is 380 V.

Step 2

Draw a neat, labelled voltage phasor diagram that represents a three-phase delta-connected system.

99%

104 rated

Answer

The voltage phasor diagram for a three-phase delta-connected system consists of three phasors, each separated by 120 degrees, illustrated as follows:

  1. Label each phase as VL1V_{L1}, VL2V_{L2}, and VL3V_{L3}.
  2. The angles between the phasors should be 120 degrees.

Delta Phasor Diagram

Make sure to indicate the rotation direction and label each phasor appropriately.

Step 3

Current delivered by the alternator at full load.

96%

101 rated

Answer

To determine the current delivered by the alternator at full load, we use the formula:

I_L = rac{S}{ ext{sqrt}(3) imes V_L}

Substituting the given values:

  • S=20imes103extVAS = 20 imes 10^3 ext{ VA}
  • VL=380extVV_L = 380 ext{ V}

We find:

I_L = rac{20 imes 10^3}{ ext{sqrt}(3) imes 380} ILextapproximatelyequals30,39extAI_L ext{ approximately equals } 30,39 ext{ A}

Step 4

Power rating of the alternator.

98%

120 rated

Answer

The power rating can be calculated using the power factor:

P=extsqrt(3)imesVLimesILimesextcos(heta)P = ext{sqrt}(3) imes V_L imes I_L imes ext{cos}( heta)

Where:

  • VL=380extVV_L = 380 ext{ V}
  • IL=30,39extAI_L = 30,39 ext{ A}
  • extcos(heta)=0,87 ext{cos}( heta) = 0,87 (lagging)

Substituting the values:

P=extsqrt(3)imes380imes30,39imes0,87P = ext{sqrt}(3) imes 380 imes 30,39 imes 0,87 Pextapproximatelyequals17,4extkWP ext{ approximately equals } 17,4 ext{ kW}

Step 5

State the function of a kilowatt-hour meter.

97%

117 rated

Answer

A kilowatt-hour (kWh) meter measures the amount of energy consumed over a specified period. It quantifies the total electrical energy used by a load.

Step 6

State TWO methods used to improve the power factor of a resistive inductive load.

97%

121 rated

Answer

  1. Adding power factor correcting capacitors in parallel with the load.
  2. Using synchronous motors to adjust the power factor to unity.

Step 7

Calculate the power consumed by the load.

96%

114 rated

Answer

The power consumed by the load can be calculated as:

Pn=P1+P2P_n = P_1 + P_2

Where:

  • P1=120extWP_1 = 120 ext{ W}
  • P2=50extWP_2 = 50 ext{ W}

Thus:

Pn=120+50=170extWP_n = 120 + 50 = 170 ext{ W}

Step 8

TWO advantages of using the two-wattmeter method when measuring power of a balanced load.

99%

104 rated

Answer

  1. The power of a balanced load can be measured accurately using only two wattmeters instead of three, reducing both costs and complexity.
  2. It allows for determination of power factor in both balanced and unbalanced conditions.