In a balanced three-phase delta-connected circuit, the phase voltage is 380 V and the phase current is 12 A - NSC Electrical Technology Electronics - Question 2 - 2017 - Paper 1

Question icon

Question 2

In-a-balanced-three-phase-delta-connected-circuit,-the-phase-voltage-is-380-V-and-the-phase-current-is-12-A-NSC Electrical Technology Electronics-Question 2-2017-Paper 1.png

In a balanced three-phase delta-connected circuit, the phase voltage is 380 V and the phase current is 12 A. If the phase angle is 25°, calculate the following: 2.1... show full transcript

Worked Solution & Example Answer:In a balanced three-phase delta-connected circuit, the phase voltage is 380 V and the phase current is 12 A - NSC Electrical Technology Electronics - Question 2 - 2017 - Paper 1

Step 1

2.1.1 The true power

96%

114 rated

Answer

To calculate the true power (P) in a balanced three-phase system, we use the formula:

P = rac{3 V_{Ph} I_{Ph} \cos heta}{\sqrt{3}}

Where:

  • VPh=380VV_{Ph} = 380 V (phase voltage)
  • IPh=12AI_{Ph} = 12 A (phase current)
  • heta=25° heta = 25° (phase angle)

Thus, the true power is:

P=3×380V×12A×cos(25°)=12,40kWP = \sqrt{3} \times 380 V \times 12 A \times \cos(25°) \\ = 12,40 kW

Step 2

2.1.2 The apparent power

99%

104 rated

Answer

The apparent power (S) can be calculated using:

S=3VLILS = \sqrt{3} V_{L} I_{L}

Where:

  • VL=380VV_{L} = 380 V (line voltage)
  • IL=12AI_{L} = 12 A (line current)

So, we find:

S=3×380V×12A=13,68kVAS = \sqrt{3} \times 380 V \times 12 A = 13,68 kVA

Step 3

2.2 Calculate the line voltage in star connection

96%

101 rated

Answer

In a star connection, the line voltage (V_L) can be calculated using:

VL=3VPhV_L = \sqrt{3} V_{Ph}

Given that IPh=20AI_{Ph} = 20 A and the phase angle is 30°30°, we can compute:

VL=3×220V=381,05VV_L = \sqrt{3} \times 220 V = 381,05 V

Step 4

2.3 Give ONE reason why electricity is generated in three-phase and not in single phase.

98%

120 rated

Answer

For high power generation, the three-phase system is functional and efficient because the voltages between all phases (i.e. line voltages) are the same. This ensures greater stability and efficiency in power distribution.

Step 5

2.4 Name the type of power factor that a three-phase generator has, and explain why it has such a type of power factor.

97%

117 rated

Answer

A generator has a lagging power factor due to its inductive nature. In an inductive load, the current lags behind the applied voltage, causing the phase difference.

Step 6

2.5 State the function of a kilowatt-hour meter.

97%

121 rated

Answer

The function of a kWh meter is to measure the amount of power consumed by a consumer over a period of time, which is useful for billing purposes.

Step 7

2.6 How many electrical degrees apart are the three coils placed in three-phase generation?

96%

114 rated

Answer

The three coils in three-phase generation are placed 120 degrees apart.

Step 8

2.7 Draw a voltage phasor diagram that represents a three-phase supply.

99%

104 rated

Answer

A voltage phasor diagram for a three-phase supply consists of three vectors representing phase voltages, each separated by 120 degrees. The resultant sum of these phase voltages gives a balanced three-phase system.

Step 9

2.8 Indicate whether the reading on a voltmeter when measuring an AC voltage is a maximum value, average value or effective/rms value.

96%

101 rated

Answer

The reading on a voltmeter when measuring an AC voltage is usually the effective value or rms value.