Photo AI

3.1 State the size of the angles between the phases of a balanced three-phase AC generated waveform - NSC Electrical Technology Power Systems - Question 3 - 2018 - Paper 1

Question icon

Question 3

3.1-State-the-size-of-the-angles-between-the-phases-of-a-balanced-three-phase-AC-generated-waveform-NSC Electrical Technology Power Systems-Question 3-2018-Paper 1.png

3.1 State the size of the angles between the phases of a balanced three-phase AC generated waveform. 3.2 Define the following terms: 3.2.1 Apparent power 3.2.2 Po... show full transcript

Worked Solution & Example Answer:3.1 State the size of the angles between the phases of a balanced three-phase AC generated waveform - NSC Electrical Technology Power Systems - Question 3 - 2018 - Paper 1

Step 1

3.1 State the size of the angles between the phases of a balanced three-phase AC generated waveform.

96%

114 rated

Answer

The size of the angles between the phases of a balanced three-phase AC generated waveform is 120°.

Step 2

3.2.1 Apparent power

99%

104 rated

Answer

Apparent power is defined as the product of the current and voltage in an AC circuit, not considering the effect of reactance. It is the total power drawn from the supply.

Step 3

3.2.2 Power factor

96%

101 rated

Answer

Power factor is the ratio of the active power (real power) consumed in an AC circuit to the apparent power. It indicates the efficiency with which the electrical power is used.

Step 4

3.3 State THREE advantages for the supplier when the power factor improves.

98%

120 rated

Answer

  1. Improved power factor results in reduced energy losses in the distribution system.
  2. Suppliers can avoid penalties that may be applied for low power factor.
  3. Increased capacity of the supply system, allowing for additional loads without requiring upgrades.

Step 5

3.4.1 State THREE disadvantages of single-phase AC generation.

97%

117 rated

Answer

  1. For the same frame size, single-phase generators produce less power than three-phase generators.
  2. Single-phase generation is relatively more expensive for the same amount of energy required as compared to three-phase generation.
  3. Single-phase systems do not allow for effective load balancing, which can complicate management of power supply.

Step 6

3.4.2 Explain the advantage of connecting a three-phase alternator in star.

97%

121 rated

Answer

Connecting a three-phase alternator in star allows for the creation of a neutral point which can be grounded. This configuration also enables greater flexibility in the use of phase voltages, supporting various load types.

Step 7

3.5 Explain how copper losses are reduced in overhead transmission lines.

96%

114 rated

Answer

Copper losses in overhead transmission lines are reduced by increasing the transmission voltage, which in turn decreases the current in the lines. Since losses are proportional to the square of the current, reducing the current helps minimize these losses.

Step 8

3.6.1 Phase voltage

99%

104 rated

Answer

To calculate the phase voltage in a star connection, use the formula: VP=VL3V_P = \frac{V_L}{\sqrt{3}} Substituting the given values: VP=3803=219.39 VV_P = \frac{380}{\sqrt{3}} = 219.39 \text{ V}

Step 9

3.6.2 Line current to the load

96%

101 rated

Answer

The line current can be calculated using the formula: IL=Pin3VLcosθI_L = \frac{P_{in}}{\sqrt{3} \cdot V_L \cdot \cos \theta} Substituting the given values: IL=1800033800.8=34.19 AI_L = \frac{18000}{\sqrt{3} \cdot 380 \cdot 0.8} = 34.19 \text{ A}

Step 10

3.6.3 Apparent power

98%

120 rated

Answer

The apparent power can be calculated using the formula: Sapp=3VLILS_{app} = \sqrt{3} \cdot V_L \cdot I_L Substituting the values: Sapp=338034.19=22.50 kVAS_{app} = \sqrt{3} \cdot 380 \cdot 34.19 = 22.50 \text{ kVA}

Step 11

3.7.1 Calculate the total input power to the motor.

97%

117 rated

Answer

The total input power to the motor can be calculated by summing the readings from the two wattmeters: PT=P1+P2=1.2 kW+2.3 kW=3.5 kWP_T = P_1 + P_2 = 1.2 \text{ kW} + 2.3 \text{ kW} = 3.5 \text{ kW}

Step 12

3.7.2 State THREE advantages of the two-wattmeter method over the three-wattmeter method.

97%

121 rated

Answer

  1. The two-wattmeter method is simpler and requires fewer measurements, making it easier to implement.
  2. It provides a reliable measurement method without needing to include a neutral point.
  3. It is less complicated and more cost-effective compared to the three-wattmeter method.

Join the NSC students using SimpleStudy...

97% of Students

Report Improved Results

98% of Students

Recommend to friends

100,000+

Students Supported

1 Million+

Questions answered

;