5.1 Define the term synchronous speed of the motor - NSC Electrical Technology Power Systems - Question 5 - 2019 - Paper 1

Question icon

Question 5

5.1-Define-the-term-synchronous-speed-of-the-motor-NSC Electrical Technology Power Systems-Question 5-2019-Paper 1.png

5.1 Define the term synchronous speed of the motor. 5.2 Give the reasons why the following tests are conducted: 5.2.1 Continuity test. 5.2.2 Insulation resistance... show full transcript

Worked Solution & Example Answer:5.1 Define the term synchronous speed of the motor - NSC Electrical Technology Power Systems - Question 5 - 2019 - Paper 1

Step 1

5.1 Define the term synchronous speed of the motor.

96%

114 rated

Answer

The synchronous speed of a motor is defined as the speed at which the magnetic field rotates within the stator windings. It can be calculated using the formula: N_s = rac{60 imes f}{p} where:

  • NsN_s = synchronous speed in r/min
  • ff = frequency in Hz
  • pp = number of poles.

Step 2

5.2.1 Continuity test.

99%

104 rated

Answer

The continuity test is conducted to ensure:

  • There is a complete path for electric current to flow,
  • There is continuity between the ends of each coil,
  • There is no break in the electrical connections.

Step 3

5.2.2 Insulation resistance test.

96%

101 rated

Answer

The insulation resistance test is conducted to ensure that there is no electrical connection between:

  • Each of the windings and earth,
  • Each of the windings to ensure they are insulated properly to avoid short circuits.

Step 4

5.3 Describe the operation of the squirrel-cage induction motor.

98%

120 rated

Answer

In a squirrel-cage induction motor, when a three-phase supply is connected to the stator winding, a rotating magnetic field is produced. This rotating field induces an electromotive force (e.m.f) in the rotor.

The induced current in the rotor creates its own magnetic field, which interacts with the stator's rotating field, producing a force that causes the rotor to turn in the same direction as the magnetic field. The difference in speed between the rotating magnetic field and the rotor is known as slip.

Step 5

5.4.1 Identify the interlocking contacts.

97%

117 rated

Answer

The interlocking contacts identified are MC3 (N/C) and MC2 (N/C), which prevent both contactors from being energized simultaneously.

Step 6

5.4.2 Explain why MC1 (N/O1) is connected in parallel with the start button.

97%

121 rated

Answer

MC1 (N/O1) is connected in parallel with the start button to latch and retain the circuit once the start button is pressed. It ensures that when the start button is released, the circuit remains closed, keeping the motor energized.

Step 7

5.4.3 Describe the operation of the star-delta control circuit.

96%

114 rated

Answer

When the start button is pressed, MC1 will be energized, closing MC1 (N/O1) and MC1 (N/O2). This action also energizes MC2 (N/C), allowing the motor to run in star configuration, which reduces the starting current. After a preset time, the timer will open T(N/C) and close T(N/O), de-energizing MC2 and energizing MC3, allowing the motor to continue running in delta mode for normal operation.

Step 8

5.5.1 Synchronous speed in r/min.

99%

104 rated

Answer

The synchronous speed can be calculated as follows: N_s = rac{60 imes f}{p} = rac{60 imes 50}{18} = 166.67 ext{ r/min}

Step 9

5.5.2 Percentage slip if the rotor speed is 955 r/min.

96%

101 rated

Answer

The percentage slip can be calculated using the formula: ext{Slip} = rac{N_s - N_{r}}{N_s} imes 100 where:

  • NrN_{r} = rotor speed.

Substituting the values gives: ext{Slip} = rac{166.67 - 955}{166.67} imes 100 = 4.5 ext{ \\%}