5.1 Name TWO types of transformer core constructions used in three-phase transformers - NSC Electrical Technology Power Systems - Question 5 - 2022 - Paper 1

Question icon

Question 5

5.1-Name-TWO-types-of-transformer-core-constructions-used-in-three-phase-transformers-NSC Electrical Technology Power Systems-Question 5-2022-Paper 1.png

5.1 Name TWO types of transformer core constructions used in three-phase transformers. 5.2 Explain why dielectric oil is used inside a transformer. 5.3 State where... show full transcript

Worked Solution & Example Answer:5.1 Name TWO types of transformer core constructions used in three-phase transformers - NSC Electrical Technology Power Systems - Question 5 - 2022 - Paper 1

Step 1

5.1 Name TWO types of transformer core constructions used in three-phase transformers.

96%

114 rated

Answer

Two types of transformer core constructions commonly used in three-phase transformers are:

  1. Core-type: In this construction, the magnetic core is made of laminated sheets, providing a closed magnetic path.
  2. Shell-type: This design encases the winding within the core, which allows for better electromagnetic coupling and reduced losses.

Step 2

5.2 Explain why dielectric oil is used inside a transformer.

99%

104 rated

Answer

Dielectric oil serves two primary purposes in a transformer. Firstly, it acts as a non-conductor of electricity, providing essential electrical insulation between the winding and the transformer's metallic parts. Secondly, it provides cooling support, helping to maintain optimal operating temperatures by dissipating heat generated during the transformation process.

Step 3

5.3 State where the Buchholz relay is situated in an oil-cooled transformer.

96%

101 rated

Answer

The Buchholz relay is strategically placed in-line between the conservator and the transformer housing. This positioning allows it to monitor gas accumulation within the transformer, functioning as an important safety device that detects abnormal conditions such as overheating or faults.

Step 4

5.4 Draw a three-phase delta-star step-down transformer unit by using three identical single-phase transformers.

98%

120 rated

Answer

To represent a three-phase delta-star step-down transformer, you can draw three identical single-phase transformers arranged in a delta configuration on the primary side and a star configuration on the secondary side. Ensure to label each winding and indicate the common neutral connection on the secondary side.

Step 5

5.5.1 Output power

97%

117 rated

Answer

The output power can be calculated using the formula:

P=Simesextp.f.P = S imes ext{p.f.}

Substituting the given values:

P=10,000extVAimes0.8=8,000extWP = 10,000 ext{ VA} imes 0.8 = 8,000 ext{ W}

Thus, the output power of the transformer is 8,000 W.

Step 6

5.5.2 Efficiency

97%

121 rated

Answer

The efficiency of the transformer can be calculated using the formula:

extEfficiency(extη)=PoutPout+extlosses×100 ext{Efficiency} ( ext{η}) = \frac{P_{out}}{P_{out} + ext{losses}} \times 100

Where the losses are the sum of the copper loss and core loss: losses=300extW+50extW=350extW\text{losses} = 300 ext{ W} + 50 ext{ W} = 350 ext{ W} Substituting the values:

η=8,0008,000+350×10095.8%η = \frac{8,000}{8,000 + 350} \times 100 \approx 95.8 \%

Therefore, the efficiency is approximately 95.8%.

Step 7

5.6.1 Rating of the transformer (apparent kVA)

96%

114 rated

Answer

To find the apparent power (kVA), we use:

S=3×VL×ILS = \sqrt{3} \times V_L \times I_L

Where:

  • VL=6,000extVV_L = 6,000 ext{ V}
  • IL=2extAI_L = 2 ext{ A}

Calculating:

S=3×6,000×2=20,784.61 VA20.78 kVAS = \sqrt{3} \times 6,000 \times 2 = 20,784.61 \text{ VA} \approx 20.78 \text{ kVA}

Thus, the rating of the transformer is approximately 20.78 kVA.

Step 8

5.6.2 Power factor of the load

99%

104 rated

Answer

The power factor (pf) can be calculated using:

pf=PS\text{pf} = \frac{P}{S}

Where: P=18,000extWP = 18,000 ext{ W} S=20,784.61 VAS = 20,784.61 \text{ VA} Substituting the values:

pf=18,00020,784.610.87\text{pf} = \frac{18,000}{20,784.61} \approx 0.87

Hence, the power factor of the load is approximately 0.87.

Step 9

5.6.3 Primary phase voltage

96%

101 rated

Answer

In a delta configuration, the line voltage (VLV_L) is equal to the phase voltage (VphV_{ph}) related by:

VL=VphV_{L} = V_{ph}

For this transformer:

  • Given: VL=6,000extVV_L = 6,000 ext{ V}, therefore,
  • Vph=6,000extVV_{ph} = 6,000 ext{ V}.

Step 10

5.6.4 Turns ratio

98%

120 rated

Answer

The turns ratio can be calculated using:

TR=Vph(1)Vph(2)\text{TR} = \frac{V_{ph(1)}}{V_{ph(2)}}

For the primary and secondary voltage values:

  • Given: Vph(1)=6,000extVV_{ph(1)} = 6,000 ext{ V} and Vph(2)=240extVV_{ph(2)} = 240 ext{ V},

Calculating: TR=6,000240=25\text{TR} = \frac{6,000}{240} = 25

Thus, the turns ratio is 25.