5.1 Explain the principle of mutual induction with reference to transformers - NSC Electrical Technology Power Systems - Question 5 - 2022 - Paper 1

Question icon

Question 5

5.1-Explain-the-principle-of-mutual-induction-with-reference-to-transformers-NSC Electrical Technology Power Systems-Question 5-2022-Paper 1.png

5.1 Explain the principle of mutual induction with reference to transformers. 5.2 Single-phase transformers can be used to create a three-phase transformer unit. An... show full transcript

Worked Solution & Example Answer:5.1 Explain the principle of mutual induction with reference to transformers - NSC Electrical Technology Power Systems - Question 5 - 2022 - Paper 1

Step 1

Explain the principle of mutual induction with reference to transformers.

96%

114 rated

Answer

Mutual induction occurs when the magnetic flux from one coil cuts the conductors of another adjacent coil, inducing an electromotive force (emf) in that coil without any electrical connections between them. This principle is fundamental in transformers, enabling the transfer of energy from one coil to another via the magnetic field.

Step 2

List THREE characteristics of single-phase transformers that must be identical.

99%

104 rated

Answer

  1. Transformer ratio: The turns ratio needs to be equal for optimal performance across all phases.
  2. Voltage rating: All transformers must have the same voltage rating to ensure compatibility and safety.
  3. Current rating: All transformers must have identical current ratings to maintain balance during operation.

Step 3

Name the connection on the secondary side of a three-phase transformer that will create a neutral point.

96%

101 rated

Answer

The secondary side connection that will create a neutral point is the Star (Y) connection.

Step 4

Discuss the main contributing factors for the following losses in transformers: Copper losses.

98%

120 rated

Answer

Copper losses refer to the energy lost in the form of heat due to the resistance of the copper conductors in the transformer windings when current flows. These losses are proportional to the square of the current flowing, mathematically represented as:

Pcopper=I2RP_{copper} = I^2 R where PcopperP_{copper} is the power loss, II is the current, and RR is the resistance.

Step 5

Discuss the main contributing factors for the following losses in transformers: Iron losses.

97%

117 rated

Answer

Iron losses, also known as core losses, occur due to the eddy currents and the changing magnetic field within the core material. These losses are influenced by the frequency of the electrical supply and are typically made up of hysteresis losses and eddy current losses, both resulting in energy dissipation as heat.

Step 6

Describe how insulation failure is controlled in dry-type transformers.

97%

121 rated

Answer

Insulation failure in dry-type transformers is controlled by using materials that are resistant to degradation from heat and environmental factors. Furthermore, proper design includes strategies such as installing ventilation systems to maintain an optimal thermal environment and regular maintenance checks to inspect and replace aging insulation materials.

Step 7

Differentiate between shell-type and core-type transformers with reference to the core.

96%

114 rated

Answer

In a shell-type transformer, the core surrounds the coils and the coils are wound around three limbs of the core. Conversely, in a core-type transformer, the core is structured with three limbs, and the coils are wound around the central part of the core, allowing for better magnetic flux utilization.

Step 8

Describe how a balanced earth-fault relay protects a three-phase transformer.

99%

104 rated

Answer

A balanced earth-fault relay monitors the current flowing through the three phases. Under normal conditions, the three-phase currents sum to zero. However, if there is an earth fault in one of the phases, the difference in current will trigger the relay. This action isolates the transformer from the power supply, thus protecting it from damage.

Step 9

Calculate the Secondary line current.

96%

101 rated

Answer

To calculate the secondary line current (IL2I_L2), we use the formula:

IL2=Pload3VL2cosθI_L2 = \frac{P_{load}}{\sqrt{3} \cdot V_{L2} \cdot \cos \theta} Plugging in the values: IL2=20000034000.8=360.84AI_L2 = \frac{200000}{\sqrt{3} \cdot 400 \cdot 0.8} = 360.84\, A

Step 10

Calculate the Secondary phase current.

98%

120 rated

Answer

In a star connection, the line current equals the phase current, so:

Ip2=IL2=360.84AI_{p2} = I_{L2} = 360.84\, A

Step 11

Calculate the Apparent power.

97%

117 rated

Answer

The apparent power (SS) can be calculated using the formula:

S=PloadcosθS = \frac{P_{load}}{\cos \theta} Substituting the given values: S=2000000.8=250000VAS = \frac{200000}{0.8} = 250000\, VA

Step 12

Calculate the Primary line current.

97%

121 rated

Answer

To find the primary line current (IL1I_{L1}), we use the formula:

IL1=P3VL1cosθI_{L1} = \frac{P}{\sqrt{3} \cdot V_{L1} \cdot \cos \theta} Substituting the values: IL1=200000360000.8=24.06AI_{L1} = \frac{200000}{\sqrt{3} \cdot 6000 \cdot 0.8} = 24.06\, A