6.1 Name the TWO types of rotor construction used in induction motors - NSC Electrical Technology Power Systems - Question 6 - 2022 - Paper 1

Question icon

Question 6

6.1-Name-the-TWO-types-of-rotor-construction-used-in-induction-motors-NSC Electrical Technology Power Systems-Question 6-2022-Paper 1.png

6.1 Name the TWO types of rotor construction used in induction motors. 6.2 Refer to the speed of induction motors and answer the questions that follow. 6.2.1 Expla... show full transcript

Worked Solution & Example Answer:6.1 Name the TWO types of rotor construction used in induction motors - NSC Electrical Technology Power Systems - Question 6 - 2022 - Paper 1

Step 1

6.1 Name the TWO types of rotor construction used in induction motors.

96%

114 rated

Answer

The two types of rotor construction used in induction motors are:

  • Wound rotor
  • Cage rotor

Step 2

6.2.1 Explain the difference between rated speed and full-load speed.

99%

104 rated

Answer

Rated speed is the maximum speed at which the motor effectively works under no load or minimal load. Conversely, full-load speed is the speed when the motor is under maximum load. Full-load speed is usually lower than the rated speed due to the load's impact on the motor's performance.

Step 3

6.2.2 Calculate the synchronous speed of a three-phase motor with four pole pairs per phase that are connected to a 400 V/50 Hz supply.

96%

101 rated

Answer

The synchronous speed can be calculated using the formula: n_s = rac{60 imes f}{p} where:

  • ff is the frequency (50 Hz),
  • pp is the number of poles (which is 2 times the number of pole pairs).
    Thus, p=2imes4=8p = 2 imes 4 = 8.
    Now substituting the values: n_s = rac{60 imes 50}{8} = 375 ext{ r/min}.

Step 4

6.2.3 Calculate the percentage slip if the rotor turns at 725 r/min (rpm).

98%

120 rated

Answer

The percentage slip can be calculated using the formula: ext{Slip} = rac{n_s - n_r}{n_s} imes 100 where:

  • nsn_s is the synchronous speed (750 r/min from previous calculation),
  • nrn_r is the rotor speed (725 r/min).
    Substituting these into the formula: ext{Slip} = rac{750 - 725}{750} imes 100 = 3.33\%.

Step 5

6.3 Name TWO mechanical inspections that could be carried out on the rotor and bearings of a motor.

97%

117 rated

Answer

Two mechanical inspections that could be carried out on the rotor and bearings are:

  1. Checking if there is any play on the axis.
  2. Checking if the bearings work smoothly when turned by hand.

Step 6

6.4.1 Input power.

97%

121 rated

Answer

The input power can be calculated using the formula:

oot{3}}{ oot{3}} I_L V_L ext{cos } \theta$$ Substituting the known values: $$P = rac{ oot{3}}{1} imes 5 imes 380 imes ext{cos } 20º = 3092.43 ext{ W}$$.

Step 7

6.4.2 Reactive power.

96%

114 rated

Answer

The reactive power is calculated using:

oot{3}}{1} I_L V_L ext{sin } \theta$$ Substituting: $$Q = rac{ oot{3}}{1} imes 5 imes 380 imes ext{sin } 20º = 1125.55 ext{ Var}$$.

Step 8

6.4.3 Output power if the motor is 90% efficient.

99%

104 rated

Answer

The output power can be determined using: P_{ ext{output}} = P_{ ext{input}} imes rac{90}{100} Substituting the input power: Pextoutput=3092.43imes0.9=2783.19extWP_{ ext{output}} = 3092.43 imes 0.9 = 2783.19 ext{ W}.

Step 9

6.5 Redraw the terminal box in the ANSWER BOOK and indicate how the motor can be connected in delta.

96%

101 rated

Answer

To connect the motor in delta, the terminals should be connected as follows:

  • Connect W1 to U2, U1 to V2, and V1 to W2.
    Ensure that each terminal is wired correctly to allow the three-phase supply to flow effectively.

Step 10

6.6.1 Identify component A.

98%

120 rated

Answer

Component A is identified as the overload relay, which is a Normally Closed (N/C) contact.

Step 11

6.6.2 Explain the purpose of MC1/N.O2.

97%

117 rated

Answer

MC1/N.O2 is a hold-out contact ensuring that the timer relay and the star contactor MC2 do not energise until MC1 is energised.

Step 12

6.6.3 Explain the importance of interlocking in this circuit.

97%

121 rated

Answer

Interlocking ensures that MC2 and MC3 do not energise simultaneously, preventing potential faults in the system.

Step 13

6.6.4 Describe the operation of the circuit after the timer has timed through.

96%

114 rated

Answer

Once the timer has timed out, the Normally Closed (N/C) contact will open, de-energising MC2. This action will close MC2/N.C and T/N.O, ensuring that MC3 remains de-energised, thus completing the circuit's operational sequence.