Photo AI

2.1 Name the instrument that is used to measure electrical energy - NSC Electrical Technology Power Systems - Question 2 - 2016 - Paper 1

Question icon

Question 2

2.1-Name-the-instrument-that-is-used-to-measure-electrical-energy-NSC Electrical Technology Power Systems-Question 2-2016-Paper 1.png

2.1 Name the instrument that is used to measure electrical energy. 2.2 State TWO advantages of three-phase systems over single-phase systems. 2.3 Draw a neatly lab... show full transcript

Worked Solution & Example Answer:2.1 Name the instrument that is used to measure electrical energy - NSC Electrical Technology Power Systems - Question 2 - 2016 - Paper 1

Step 1

Name the instrument that is used to measure electrical energy.

96%

114 rated

Answer

The instrument used to measure electrical energy is a Kilo-watt hour meter.

Step 2

State TWO advantages of three-phase systems over single-phase systems.

99%

104 rated

Answer

  1. Three-phase systems can be operated in star or delta configurations, allowing for versatile system designs.
  2. Three-phase systems can supply both three-phase and single-phase loads, offering greater flexibility in applications.

Step 3

Draw a neatly labelled sketch representing the voltage waveforms of a three-phase AC generation system.

96%

101 rated

Answer

A labelled sketch should depict three sine waveforms offset by 120 degrees each, demonstrating the amplitude and the displacement of the waveforms across the phases (Ph1, Ph2, and Ph3).

Step 4

Calculate the Line voltage.

98%

120 rated

Answer

To find the line voltage (VLV_L), we use the formula: S = rac{ ext{√3} imes I_L imes V_L}{S} Substituting the known values: V_L = rac{S}{ ext{√3} imes I_L} = rac{20000}{ ext{√3} imes 25} = 461.88 ext{ V}

Step 5

Calculate the Phase voltage.

97%

117 rated

Answer

To calculate the phase voltage (VpV_p), we use: V_p = rac{V_L}{ ext{√3}} = rac{461.88}{ ext{√3}} = 267.67 ext{ V}

Step 6

Calculate the Total input power.

97%

121 rated

Answer

Total input power (PTP_T) is calculated as: PT=P1+P2=8extkW+4extkW=12extkWP_T = P_1 + P_2 = 8 ext{ kW} + 4 ext{ kW} = 12 ext{ kW}

Step 7

Calculate the Line current.

96%

114 rated

Answer

Using the formula for line current (ILI_L): P=ext3imesVLimesILimesextCosφP = ext{√3} imes V_L imes I_L imes ext{Cos φ} Rearranging gives: I_L = rac{P}{ ext{√3} imes V_L imes ext{Cos φ}} = rac{12000}{ ext{√3} imes 380 imes 0.8} = 22.79 A

Join the NSC students using SimpleStudy...

97% of Students

Report Improved Results

98% of Students

Recommend to friends

100,000+

Students Supported

1 Million+

Questions answered

;