Photo AI

3.1 List THREE advantages of power factor improvement for the consumer - NSC Electrical Technology Power Systems - Question 3 - 2019 - Paper 1

Question icon

Question 3

3.1-List-THREE-advantages-of-power-factor-improvement-for-the-consumer-NSC Electrical Technology Power Systems-Question 3-2019-Paper 1.png

3.1 List THREE advantages of power factor improvement for the consumer. 3.2 Explain why the power distribution to consumers is connected in star. 3.3 State the dif... show full transcript

Worked Solution & Example Answer:3.1 List THREE advantages of power factor improvement for the consumer - NSC Electrical Technology Power Systems - Question 3 - 2019 - Paper 1

Step 1

3.1 List THREE advantages of power factor improvement for the consumer.

96%

114 rated

Answer

  1. Less Current Used: By improving the power factor, the amount of current flowing in the system is reduced, leading to lower losses in wiring and equipment.
  2. Reduced Monthly Bill: Utilities may charge less for customers with better power factors, resulting in lower electricity costs.
  3. Reduced Heat Generation: Improved power factor results in less heat generated by electrical equipment, which can prolong the lifespan of the equipment.

Step 2

3.2 Explain why the power distribution to consumers is connected in star.

99%

104 rated

Answer

The star connection in power distribution systems allows for a neutral point, which can be used to provide single-phase power as needed to consumers. This configuration also helps in maintaining a balanced load across all three phases and provides a return path for unbalanced currents, ensuring stable operation.

Step 3

3.3 State the difference between a wattmeter and a kilowatt-hour meter.

96%

101 rated

Answer

A wattmeter measures the instantaneous power (in watts) being consumed by a load at any given moment, while a kilowatt-hour meter records the total energy consumed over time, measured in kilowatt-hours, which accounts for both the load and the duration of its operation.

Step 4

3.4 State the purpose of the following:

98%

120 rated

Answer

3.4.1 National Power Grid: The National Grid transmits electrical power from generation sources to consumers efficiently and reliably.
3.4.2 Eskom's National Control Centres: These centres monitor and control the National Grid's operation, ensuring stability, managing supply and demand, and coordinating maintenance and outage schedules.

Step 5

3.5.1 Label the generated voltage waveforms marked 2 and 3 according to the universally adopted sequence.

97%

117 rated

Answer

Using the reference waveform marked as Vr:
2: Voltage waveform of Phase 2 (Vb)
3: Voltage waveform of Phase 3 (Vc)

Step 6

3.5.2 Name the phase displacement between the three waveforms generated in FIGURE 3.5.

97%

121 rated

Answer

The phase displacement between the three waveforms is 120°.

Step 7

3.6.1 Input power

96%

114 rated

Answer

To find the input power, use the formula:
Pin=PoutηP_{in} = \frac{P_{out}}{\eta}
Where:
Pout=25kW,η=0.85P_{out} = 25 \, kW, \quad \eta = 0.85
Therefore:
Pin=25kW0.8529.41kWP_{in} = \frac{25 \, kW}{0.85} \approx 29.41 \, kW

Step 8

3.6.2 Line current.

99%

104 rated

Answer

To find the line current, use the formula:
IL=Pin3VLcosϕI_L = \frac{P_{in}}{\sqrt{3} V_L \cos \phi}
Where:
Pin29.41kW,VL=380V,cosϕ=0.87P_{in} \approx 29.41 \, kW, \quad V_L = 380 \, V, \quad \cos \phi = 0.87
Calculating gives:
IL=29.41×1033×380×0.8751.36AI_L = \frac{29.41 \times 10^3}{\sqrt{3} \times 380 \times 0.87} \approx 51.36 \, A

Step 9

3.6.3 Phase current.

96%

101 rated

Answer

The phase current can be calculated as:
IPH=IL=51.36AI_{PH} = I_L = 51.36 \, A

Step 10

3.7.1 Identify the method used in FIGURE 3.7 to measure the power to the load.

98%

120 rated

Answer

The method used is the two wattmeter method.

Step 11

3.7.2 Calculate the total power used by the load.

97%

117 rated

Answer

To find the total power used by the load, we sum the individual powers:
PT=P1+P2=14kW+18kW=32kWP_T = P_1 + P_2 = 14 \, kW + 18 \, kW = 32 \, kW

Step 12

3.7.3 Calculate the power factor of the system.

97%

121 rated

Answer

To find the power factor, we use the formula:
tanϕ=P1P2P1+P2=141814+18tanϕ0.22\tan\phi = \frac{P_1 - P_2}{P_1 + P_2} = \frac{14 - 18}{14 + 18} \Rightarrow \tan\phi \approx -0.22
Thus,
ϕtan1(0.22)12.41°\phi \approx \tan^{-1}(-0.22) \approx -12.41°
The power factor is then given by:
PF=cos(12.41°)0.98PF = \cos(-12.41°) \approx 0.98

Step 13

3.8 Calculate the line current at full load.

96%

114 rated

Answer

To calculate the line current at full load, use:
S=3VLILS = \sqrt{3} V_L I_L
Given:
S=20kVA,VPH=220VS = 20 \, kVA, \quad V_{PH} = 220 \, V
Then,
IL=20×1033×22052.5AI_L = \frac{20 \times 10^3}{\sqrt{3} \times 220} \approx 52.5 \, A

Join the NSC students using SimpleStudy...

97% of Students

Report Improved Results

98% of Students

Recommend to friends

100,000+

Students Supported

1 Million+

Questions answered

;