Photo AI

FIGURE 4.1 below shows a block diagram of the national power grid in South Africa - NSC Electrical Technology Power Systems - Question 4 - 2024 - Paper 1

Question icon

Question 4

FIGURE-4.1-below-shows-a-block-diagram-of-the-national-power-grid-in-South-Africa-NSC Electrical Technology Power Systems-Question 4-2024-Paper 1.png

FIGURE 4.1 below shows a block diagram of the national power grid in South Africa. Answer the questions that follow. FIGURE 4.1: NATIONAL POWER GRID 4.1.1 State th... show full transcript

Worked Solution & Example Answer:FIGURE 4.1 below shows a block diagram of the national power grid in South Africa - NSC Electrical Technology Power Systems - Question 4 - 2024 - Paper 1

Step 1

4.1.1 State the voltage generated at block A.

96%

114 rated

Answer

The voltage generated at block A is 22 kV.

Step 2

4.1.2 Name the standard international colour code for a three-phase system with reference to each phase.

99%

104 rated

Answer

The standard international colour code for a three-phase system is as follows:

  • Phase 1 - Red
  • Phase 2 - Yellow
  • Phase 3 - Blue

Step 3

4.1.3 Briefly describe the national grid.

96%

101 rated

Answer

The national grid is a network of over 25,000 km of high voltage power lines that allows electricity to be generated, transmitted, and distributed across the country.

Step 4

4.1.4 Explain why the transmission of electricity is done at such high voltages.

98%

120 rated

Answer

Electricity is transmitted at high voltages to decrease the current flowing in the transmission lines, which reduces the copper losses associated with power transmission.

Step 5

4.1.5 Explain how the voltage for an industrial consumer is different from the voltage for a domestic consumer.

97%

117 rated

Answer

An industrial consumer typically uses a three-phase voltage of 400 V, while domestic consumers use a single-phase voltage of 230 V.

Step 6

4.2 Give TWO reasons why an industrial consumer would prefer a three-phase supply over a single-phase supply.

97%

121 rated

Answer

  1. A three-phase system is more economical and efficient for powering large machinery.
  2. A three-phase system can supply both three-phase and single-phase installations, offering flexibility in usage.

Step 7

4.3.1 Calculate the line current.

96%

114 rated

Answer

The line current can be calculated using the formula:

S=3VLILS = \sqrt{3} \cdot V_L \cdot I_L

Thus,

IL=S3VL=200,0003400=288.68AI_L = \frac{S}{\sqrt{3} \cdot V_L} = \frac{200,000}{\sqrt{3} \cdot 400} = 288.68 \, A

Step 8

4.3.2 Calculate the phase current.

99%

104 rated

Answer

The phase current can be calculated as follows:

IPH=IL3=288.683=166.67AI_{PH} = \frac{I_L}{\sqrt{3}} = \frac{288.68}{\sqrt{3}} = 166.67 \, A

Step 9

4.3.3 Calculate the power factor.

96%

101 rated

Answer

The power factor can be calculated using:

Cosϕ=PS=180,000200,000=0.9Cos \phi = \frac{P}{S} = \frac{180,000}{200,000} = 0.9

Step 10

4.3.4 Calculate the reactive power.

98%

120 rated

Answer

To find the reactive power, we use:

θ=cos1(0.9)=25.84°\theta = \cos^{-1}(0.9) = 25.84°

Then,

Q=S2P2=(200,000)2(180,000)287.17kVArQ = \sqrt{S^2 - P^2} = \sqrt{(200,000)^2 - (180,000)^2} \approx 87.17 \, kVAr

Step 11

4.4.1 State where power factor correcting devices may be installed.

97%

117 rated

Answer

Power factor correcting devices may be installed at central substations or built into power consuming equipment.

Step 12

4.4.2 Identify ONE improvement with reference to FIGURE 4.4 above.

97%

121 rated

Answer

One improvement could be the reduction of reactive power.

Step 13

4.4.3 Explain how power factor correction affected the current drawn from the supply.

96%

114 rated

Answer

Power factor correction reduces the phase angle and apparent power, which decreases the total current drawn from the supply while keeping the load and supply voltage stable.

Step 14

4.5 Differentiate between wattmeters and energy meters with reference to their applications.

99%

104 rated

Answer

Wattmeters are used to measure instantaneous power in circuits, while energy meters measure the total electrical energy consumed over a specific period.

Step 15

4.6 Two wattmeters are used to measure the total power of a three-phase system.

96%

101 rated

Answer

The reading of the second wattmeter can be calculated as:

P2=PtotalP1=35001300=2200WP_2 = P_{total} - P_1 = 3500 - 1300 = 2200 \, W

Join the NSC students using SimpleStudy...

97% of Students

Report Improved Results

98% of Students

Recommend to friends

100,000+

Students Supported

1 Million+

Questions answered

;