In a balanced three-phase delta-connected circuit, the phase voltage is 380 V and the phase current is 12 A - NSC Electrical Technology Power Systems - Question 2 - 2017 - Paper 1

Question icon

Question 2

In-a-balanced-three-phase-delta-connected-circuit,-the-phase-voltage-is-380-V-and-the-phase-current-is-12-A-NSC Electrical Technology Power Systems-Question 2-2017-Paper 1.png

In a balanced three-phase delta-connected circuit, the phase voltage is 380 V and the phase current is 12 A. If the phase angle is 25°, calculate the following: 2.1... show full transcript

Worked Solution & Example Answer:In a balanced three-phase delta-connected circuit, the phase voltage is 380 V and the phase current is 12 A - NSC Electrical Technology Power Systems - Question 2 - 2017 - Paper 1

Step 1

2.1.1 The true power

96%

114 rated

Answer

To calculate the true power (P) in a three-phase system, we can use the formula:

P = rac{3 imes V_{L} imes I_{ph} imes ext{cos} heta}{1}

Here, the line voltage (V_{L}) is 380 V, the phase current (I_{ph}) is 12 A, and the phase angle (θ) is 25°.

Using the values:

= 3 imes 380 imes 12 imes 0.9063 \ = 12,402.06 ext{ W} ext{ or } 12.4 ext{ kW} $$

Step 2

2.1.2 The apparent power

99%

104 rated

Answer

The apparent power (S) can be calculated using:

S = rac{P}{ ext{cos} heta}

So first, we need to calculate the apparent power based on the line voltage:

S = rac{3 imes V_{L} imes I_{ph}}{1}

Using the known values:

S = rac{3 imes 380 imes 12}{1} = 13,680 ext{ VA or } 13.68 ext{ kVA}

Step 3

2.2 Calculate the line voltage

96%

101 rated

Answer

To find the line voltage (V_{L}) when the alternator is connected in star:

= 220 imes ext{sqrt}(3) \ = 381.05 ext{ V} $$

Step 4

2.3 Give ONE reason why electricity is generated in three-phase and not in single phase.

98%

120 rated

Answer

Electricity is generated in three-phase because it is more efficient for power generation. The three-phase system provides a constant power output, minimizing fluctuations, which enhances the performance of electrical machines.

Step 5

2.4 Name the type of power factor.

97%

117 rated

Answer

A three-phase generator typically has a lagging power factor due to the inductive nature of the coils. This occurs because the current lags behind the voltage in inductive loads.

Step 6

2.5 State the function of a kilowatt-hour meter.

97%

121 rated

Answer

The function of a kilowatt-hour (kWh) meter is to measure the amount of electrical energy consumed by a consumer over time, typically in kilowatt-hours.

Step 7

2.6 How many electrical degrees apart are the three coils placed in three-phase generation?

96%

114 rated

Answer

The three coils in three-phase generation are placed 120 degrees apart from each other.

Step 8

2.7 Draw a voltage phasor diagram.

99%

104 rated

Answer

The voltage phasor diagram for a three-phase system consists of three vectors (phasors) representing the voltages of each phase placed 120 degrees apart, showing their direction of rotation.

Step 9

2.8 Indicate whether the reading on a voltmeter is a maximum value, average value or effective/rms value.

96%

101 rated

Answer

The reading on a voltmeter when measuring an AC voltage is typically an effective value or rms (root mean square) value.