4.1.1 State the voltage generated at block A - NSC Electrical Technology Power Systems - Question 4 - 2024 - Paper 1

Question icon

Question 4

4.1.1-State-the-voltage-generated-at-block-A-NSC Electrical Technology Power Systems-Question 4-2024-Paper 1.png

4.1.1 State the voltage generated at block A. 4.1.2 Name the standard international colour code for a three-phase system with reference to each phase. 4.1.3 Briefl... show full transcript

Worked Solution & Example Answer:4.1.1 State the voltage generated at block A - NSC Electrical Technology Power Systems - Question 4 - 2024 - Paper 1

Step 1

State the voltage generated at block A.

96%

114 rated

Answer

The voltage generated at block A is 22 kV.

Step 2

Name the standard international colour code for a three-phase system with reference to each phase.

99%

104 rated

Answer

The standard international colour code for a three-phase system is as follows:

  • Phase 1 - Red
  • Phase 2 - Yellow
  • Phase 3 - Blue

Step 3

Briefly describe the national grid.

96%

101 rated

Answer

The national grid is a network of over 25,000 km of high voltage power lines for various bulk users. It facilitates the generation, transmission, and distribution of electricity across regions.

Step 4

Explain why the transmission of electricity is done at such high voltages.

98%

120 rated

Answer

Electricity is transmitted at high voltages to reduce power losses in transmission lines. Higher voltage reduces the current flowing through the lines, minimizing heat losses due to resistance.

Step 5

Explain how the voltage for an industrial consumer is different from the voltage for a domestic consumer.

97%

117 rated

Answer

Industrial consumers typically utilize a three-phase voltage of 400 V, while domestic consumers receive a single-phase voltage of 230 V, as the industrial load requires higher power levels.

Step 6

Give TWO reasons why an industrial consumer would prefer a three-phase supply over a single-phase supply.

97%

121 rated

Answer

  1. A three-phase system is more economical for supplying power, especially for larger loads.
  2. It allows for efficient supply of both three-phase and single-phase installations, which aids in better load balancing.

Step 7

Calculate the line current.

96%

114 rated

Answer

The line current can be calculated using the formula: S=3VLILS = \sqrt{3} V_L I_L Given: S = 200 kVA, VLV_L = 400 V, we have: IL=S3VL=200×1033×400=288.68AI_L = \frac{S}{\sqrt{3} V_L} = \frac{200 \times 10^3}{\sqrt{3} \times 400} = 288.68 A

Step 8

Calculate the phase current.

99%

104 rated

Answer

The phase current can be calculated using: IPH=IL3=288.683=166.67AI_{PH} = \frac{I_L}{\sqrt{3}} = \frac{288.68}{\sqrt{3}} = 166.67 A

Step 9

Calculate the power factor.

96%

101 rated

Answer

The power factor can be calculated using: Cosϕ=PS=180,000200,000=0.9Cos \phi = \frac{P}{S} = \frac{180,000}{200,000} = 0.9

Step 10

Calculate the reactive power.

98%

120 rated

Answer

Using the power factor calculated: \theta = \cos^{-1}(0.9) \approx 25.84^\circ \ The reactive power is: Q=S2P2=(200,000)2(180,000)2=87.17kVArQ = \sqrt{S^2 - P^2} = \sqrt{(200,000)^2 - (180,000)^2} = 87.17 kVAr

Step 11

State where power factor correcting devices may be installed.

97%

117 rated

Answer

Power factor correcting devices can be installed at a central substation.

Step 12

Identify ONE improvement with reference to FIGURE 4.4 above.

97%

121 rated

Answer

One improvement is the reduced reactive power after power factor correction.

Step 13

Explain how power factor correction affected the current drawn from the supply.

96%

114 rated

Answer

Power factor correction reduces the phase angle and the apparent power. It leads to a lower current drawn from the supply due to better energy efficiency.

Step 14

Differentiate between wattmeters and energy meters with reference to their applications.

99%

104 rated

Answer

Wattmeters measure the instantaneous power in watts, while energy meters measure the total energy consumed over time, usually in kilowatt-hours (kWh).

Step 15

Determine the reading of meter 2.

96%

101 rated

Answer

If the total power is 3.5 kW (3500 W) and meter 1 reads 300 W, then the reading of meter 2 is: P2=PtotalP1=3500300=3200WP_2 = P_{total} - P_1 = 3500 - 300 = 3200 W