State the size of the angles between the phases of a balanced three-phase AC generated waveform - NSC Electrical Technology Power Systems - Question 3 - 2018 - Paper 1
Question 3
State the size of the angles between the phases of a balanced three-phase AC generated waveform.
Define the following terms:
3.1.1 Apparent power
3.1.2 Power facto... show full transcript
Worked Solution & Example Answer:State the size of the angles between the phases of a balanced three-phase AC generated waveform - NSC Electrical Technology Power Systems - Question 3 - 2018 - Paper 1
Step 1
3.1 State the size of the angles between the phases of a balanced three-phase AC generated waveform.
96%
114 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The angles between the phases of a balanced three-phase AC waveform are each 120 degrees.
Step 2
3.2.1 Apparent power
99%
104 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Apparent power (S) is defined as the product of the current (I) and the voltage (V) in an AC circuit, considering no reactance. It is measured in volt-amperes (VA) and represents the total power drawn from the supply.
Step 3
3.2.2 Power factor
96%
101 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Power factor (PF) is defined as the ratio of the active power (P) consumed in an AC circuit to the apparent power (S). It indicates the efficiency of the power usage in the circuit and is a dimensionless number between 0 and 1.
Step 4
3.3 State THREE advantages for the supplier when the power factor improves.
98%
120 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Improved power factor reduces the load on the power supply system, which means thinner supply cables are required, minimizing costs.
It minimizes the overall energy losses in the transmission lines, leading to more efficient power distribution.
Cost of maintenance and equipment can be lowered, as more efficient systems typically require less upkeep.
Step 5
3.4.1 State THREE disadvantages of single-phase AC generation.
97%
117 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Single-phase systems produce less power compared to three-phase systems for the same capacity.
Single-phase generation is generally more expensive for the same amount of energy production compared to three-phase.
A single-phase supply cannot balance loads as effectively as three-phase systems, leading to potential overload situations.
Step 6
3.4.2 Explain the advantage of connecting a three-phase alternator in star.
97%
121 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Connecting a three-phase alternator in star creates a neutral point, which allows for different phase voltages to be available. This setup can accommodate varying loads and enhances the system reliability as the neutral point can be grounded.
Step 7
3.5 Explain how copper losses are reduced in overhead transmission lines.
96%
114 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Copper losses are reduced by increasing the transmission voltage, which in turn decreases the line current. Given that power losses in conductors are proportional to the square of the current, lower currents lead to significantly reduced losses.
Step 8
3.6.1 Phase voltage
99%
104 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The phase voltage (V_p) is calculated using the formula:
Vp=3VL
Using the given line voltage of 380 V:
Vp=3380≈219.39V
Step 9
3.6.2 Line current to the load
96%
101 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The line current (I_L) is calculated using the formula:
IL=3×VL×CosθPin
For this scenario:
IL=3×380×0.818000≈34.19A
Step 10
3.6.3 Apparent power
98%
120 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The apparent power (S) can be calculated using:
S=3×VL×IL
Substituting the known values:
S=3×380×34.19≈22.50kVA
Step 11
3.7.1 Calculate the total input power to the motor.
97%
117 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The total input power (P_T) to the motor is the sum of the power readings from the wattmeters:
PT=P1+P2=1200+2300=3500W=3.5kW
Step 12
3.7.2 State THREE advantages of the two-wattmeter method over the three-wattmeter method.
97%
121 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The two-wattmeter method requires fewer instruments, making it more cost-effective and simpler to set up.
It can measure power accurately in both balanced and unbalanced three-phase systems.
It involves less complex circuitry compared to the three-wattmeter method, simplifying the measurement process.