3.1 Name and explain TWO types of losses that occur in transformers - NSC Electrical Technology Power Systems - Question 3 - 2017 - Paper 1
Question 3
3.1 Name and explain TWO types of losses that occur in transformers.
3.2 The delta-connected primary winding of a three-phase transformer is supplied with 11 kV. Th... show full transcript
Worked Solution & Example Answer:3.1 Name and explain TWO types of losses that occur in transformers - NSC Electrical Technology Power Systems - Question 3 - 2017 - Paper 1
Step 1
3.1 Name and explain TWO types of losses that occur in transformers.
96%
114 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Copper Losses: These losses occur due to the resistance of the copper conductors in the winding. When current flows through these windings, energy is lost in the form of heat, which reduces the efficiency of the transformer.
Dielectric Losses: These are losses that happen when the insulation of the windings is damaged, causing leakage currents. It mainly occurs due to the electrical field within the insulation, leading to energy dissipation.
Step 2
3.2.1 The total kVA of the load
99%
104 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
To find the total kVA of the load, we use the formula:
S=cosθP
Substituting the values:
S=0.810kW=12.5kVA
Step 3
3.2.2 The secondary line current
96%
101 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The secondary line current can be calculated using:
Is=3VscosθP
Plugging in the values:
Is=3×400V×0.810kW=18.04A
Step 4
3.2.3 The secondary phase current
98%
120 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
For a star-connected transformer, the phase current is equal to the line current:
Iph=Is=18.04A
Step 5
3.3 Describe why the secondary winding of a transformer must be connected in star if the transformer is to supply both a domestic and an industrial load.
97%
117 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Connecting the secondary winding in star allows the transformer to provide multiple voltage levels and ensures balanced load conditions. This arrangement is essential for supplying both single-phase (domestic) and three-phase (industrial) loads effectively. It facilitates a neutral point for grounding and enhances safety.
Step 6
3.4 Name THREE causes of heat build-up in transformers.
97%
121 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Overloading: When the transformer is subjected to loads beyond its rated capacity, it generates excessive heat.
Poor Cooling: Inadequate cooling mechanisms can lead to heat accumulation.
Poor Connections: Loose or damaged connections can cause additional resistance, leading to increased heat generation.
Step 7
3.5 Explain what will happen to the primary current of an ideal transformer if the load is doubled.
96%
114 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
In an ideal transformer, the primary current will also double as it is directly proportional to the load. If the load resistance decreases, leading to an increased load current, the primary side will draw more current to maintain the transformation ratio.