Photo AI

4.10 Refer to the circuit diagram in FIGURE 4.10 below and answer the questions that follow - NSC Electrical Technology Power Systems - Question 4 - 2020 - Paper 1

Question icon

Question 4

4.10-Refer-to-the-circuit-diagram-in-FIGURE-4.10-below-and-answer-the-questions-that-follow-NSC Electrical Technology Power Systems-Question 4-2020-Paper 1.png

4.10 Refer to the circuit diagram in FIGURE 4.10 below and answer the questions that follow. Given: S = 200 kVA V_{L(1)} = 11 kV V_{L(3)} = 380 V I_{L(1)} = 30 A P... show full transcript

Worked Solution & Example Answer:4.10 Refer to the circuit diagram in FIGURE 4.10 below and answer the questions that follow - NSC Electrical Technology Power Systems - Question 4 - 2020 - Paper 1

Step 1

4.10.1 Efficiency of the transformer if it operates at a power factor of 0,85 lagging.

96%

114 rated

Answer

To calculate the efficiency (η\eta) of the transformer, we first find the output power (PoutP_{out}) using the formula:

Pout=S×power factor=200kVA×0.85=170kWP_{out} = S \times \text{power factor} = 200 \, kVA \times 0.85 = 170 \, kW

Next, we apply the efficiency formula:

η=PoutPin×100\eta = \frac{P_{out}}{P_{in}} \times 100

Substituting the values:

η=170000W171800W×100=98.95%\eta = \frac{170000 \, W}{171800 \, W} \times 100 = 98.95\%

Thus, the efficiency of the transformer is approximately 98.95%.

Step 2

4.10.2 Turns ratio.

99%

104 rated

Answer

The turns ratio (TR) can be calculated using the formula:

TR=Vph(2)Vph(1)TR = \frac{V_{ph(2)}}{V_{ph(1)}}

Where:

  • Vph(2)=380VV_{ph(2)} = 380 \, V (secondary voltage)
  • Vph(1)=11000VV_{ph(1)} = 11000 \, V (primary voltage)

Substituting the values:

TR=38011000=129=1:29TR = \frac{380}{11000} = \frac{1}{29} = 1:29

Therefore, the turns ratio is 1:29.

Step 3

4.10.3 Secondary line current.

96%

101 rated

Answer

To find the secondary line current (IL(3)I_{L(3)}), we can use the following formula:

IL(3)=SVL(3)I_{L(3)} = \frac{S}{V_{L(3)}}

Substituting the values:

IL(3)=200000VA380V526.32AI_{L(3)} = \frac{200000 \, VA}{380 \, V} \approx 526.32 \, A

Thus, the secondary line current is approximately 526.32 A.

Join the NSC students using SimpleStudy...

97% of Students

Report Improved Results

98% of Students

Recommend to friends

100,000+

Students Supported

1 Million+

Questions answered

;