4.1 Name TWO cooling methods used in a dry transformer - NSC Electrical Technology Power Systems - Question 4 - 2021 - Paper 1
Question 4
4.1 Name TWO cooling methods used in a dry transformer.
4.2 State the main cause that contributes to heat generation in transformers.
4.3 State TWO safety precauti... show full transcript
Worked Solution & Example Answer:4.1 Name TWO cooling methods used in a dry transformer - NSC Electrical Technology Power Systems - Question 4 - 2021 - Paper 1
Step 1
4.4.1 Identify the type of transformer connection in FIGURE 4.4.
96%
114 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The type of transformer connection shown in FIGURE 4.4 is a Delta-Delta (Δ-Δ) connection. In this configuration, both the primary and secondary windings are connected in a delta formation, which allows for higher starting torque and better voltage regulation.
Step 2
4.4.2 Name TWO applications of the transformer in FIGURE 4.4.
99%
104 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Industrial power distribution, where the transformer steps down the voltage for machinery and equipment use.
Commercial buildings, providing power at the required voltage levels for lighting and HVAC systems.
Step 3
4.4.3 State, with a reason, whether the transformer is a step-up or step-down transformer.
96%
101 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The transformer in FIGURE 4.4 is a step-down transformer. This is indicated by the turns ratio of 5:1, meaning that the secondary voltage is lower than the primary voltage, which is typical for stepping down voltage in power applications.
Step 4
4.5.1 Economic cost.
98%
120 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Single-phase transformers are generally less expensive to manufacture and install due to their simpler design. However, when a larger power capacity is needed, three-phase transformers are more economical in terms of installation and operational cost, as they can deliver more power with fewer copper losses.
Step 5
4.5.2 Efficiency.
97%
117 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Three-phase transformers are typically more efficient than single-phase transformers. This is due to better utilization of material and lower losses in the core and windings, resulting in higher efficiency ratings even under varying load conditions.
Step 6
4.6 Describe how the Buchholz relay would protect a transformer under minor and major faulty conditions.
97%
121 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The Buchholz relay functions as a protective device that detects gas accumulation due to overheating or internal faults. Under minor faults, it triggers alarms when bubbles of gas form in the oil, indicating insulation breakdown or overheating. In major faults, such as a severe internal short circuit, it activates the trip mechanism, shutting down the transformer to prevent catastrophic failures and potential explosions.
Step 7
4.7.1 Secondary phase voltage.
96%
114 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The secondary phase voltage can be calculated using the turns ratio as follows:
V_{ph2} = rac{V_{ph1}}{TR} = rac{2000 V}{5} = 400 V
Step 8
4.7.2 Efficiency of the transformer.
99%
104 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The efficiency (
\eta) of the transformer can be determined using the formula:
η=Pout+lossesPout×100
Substituting in the values:
η=45000W+500W45000W×100=98.9%
Step 9
4.7.3 Power factor of the transformer.
96%
101 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The power factor can be calculated using the formula:
Cosθ=SP
Using the provided values:
Cosθ=50000VA45000W=0.9
Step 10
4.7.4 Current drawn by the load.
98%
120 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The current drawn by the load can be calculated using the formula:
I2=3×V2×CosθS
Substituting the relevant values gives:
I2=3×400V×0.950000VA=72.17A