3.1 State how eddy currents may be limited in the iron core of a transformer - NSC Electrical Technology Power Systems - Question 3 - 2016 - Paper 1

Question icon

Question 3

3.1-State-how-eddy-currents-may-be-limited-in-the-iron-core-of-a-transformer-NSC Electrical Technology Power Systems-Question 3-2016-Paper 1.png

3.1 State how eddy currents may be limited in the iron core of a transformer. 3.2 Name TWO similarities between a single-phase transformer and a three-phase transfo... show full transcript

Worked Solution & Example Answer:3.1 State how eddy currents may be limited in the iron core of a transformer - NSC Electrical Technology Power Systems - Question 3 - 2016 - Paper 1

Step 1

State how eddy currents may be limited in the iron core of a transformer.

96%

114 rated

Answer

Eddy currents in the iron core of a transformer can be limited by laminating and insulating the core. This construction reduces the eddy current paths, effectively lowering their magnitude and minimizing energy losses.

Step 2

Name TWO similarities between a single-phase transformer and a three-phase transformer.

99%

104 rated

Answer

Both single-phase and three-phase transformers serve the same functional operations by stepping voltage up or down. Additionally, both can be designed as either closed core or shell core types.

Step 3

State TWO factors that may cause excessive heating in a transformer.

96%

101 rated

Answer

  1. Insufficient ventilation can hinder heat dissipation, leading to higher temperatures.
  2. Constant overloading causes excessive current flow, which generates more heat than the transformer can handle.

Step 4

Name TWO applications of a delta-star connected distribution network transformer.

98%

120 rated

Answer

  1. Supply of three-phase and single-phase electricity to commercial sites.
  2. Providing power to industrial areas requiring robust energy supply systems.

Step 5

Explain the function of a transformer in a distribution network.

97%

117 rated

Answer

A transformer in a distribution network serves to adjust voltage levels to suitable values for transmission and utilization. It steps down high voltage from transmission lines to lower voltage suitable for end-users, ensuring efficiency and safety in electrical distribution.

Step 6

Primary phase voltage

97%

121 rated

Answer

Using the formula VL=VPH3V_{L} = V_{PH} \sqrt{3}, the primary phase voltage can be calculated as follows:

VPH=VL3=660033810.66 VV_{PH} = \frac{V_{L}}{\sqrt{3}} = \frac{6600}{\sqrt{3}} \approx 3810.66 \text{ V}

Step 7

Secondary phase current

96%

114 rated

Answer

The secondary phase current IPHI_{PH} is the same as the line current in this case, so:

IPH=IP=30extAI_{PH} = I_P = 30 ext{ A}

Step 8

Turns ratio

99%

104 rated

Answer

The turns ratio (Np:NsN_p:N_s) is calculated using:

NpNs=VPHVSH=660023028.7\frac{N_p}{N_s} = \frac{V_{P_{H}}}{V_{S_{H}}} = \frac{6600}{230} \approx 28.7