5.1 Name TWO parts of the cooling system in three-phase transformers - NSC Electrical Technology Power Systems - Question 5 - 2023 - Paper 1
Question 5
5.1 Name TWO parts of the cooling system in three-phase transformers.
5.2 Name the type of loss that contributes the most to heat in three-phase transformers.
5.3 ... show full transcript
Worked Solution & Example Answer:5.1 Name TWO parts of the cooling system in three-phase transformers - NSC Electrical Technology Power Systems - Question 5 - 2023 - Paper 1
Step 1
Name TWO parts of the cooling system in three-phase transformers.
96%
114 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The two parts of the cooling system in three-phase transformers are:
Radiator
Oil conservator (also referred to as a tank)
Step 2
Name the type of loss that contributes the most to heat in three-phase transformers.
99%
104 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The type of loss that contributes the most to heat in three-phase transformers is copper losses, which arise due to the resistance in the windings.
Step 3
State ONE application of a star-delta transformer in a transmission network.
96%
101 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
A star-delta transformer is commonly used in high voltage supplies to step down voltage levels, ensuring safe distribution to industrial and residential loads.
Step 4
State how eddy current losses are reduced in transformers.
98%
120 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Eddy current losses are reduced in transformers by constructing the core out of thin laminations of silicon steel, which minimizes the circulating currents.
Step 5
Explain why heat should be dissipated in transformers.
97%
117 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Heat should be dissipated in transformers to maintain the operational efficiency and reliability of the equipment. Excessive heat can degrade insulation materials, leading to failures, reduced lifespan, and potential safety hazards.
Step 6
Name the cooling method preferred for very large transformers of several hundred MVA (megavolt ampere).
97%
121 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The preferred cooling method for very large transformers is oil forced, water forced (OFWF) cooling, where oil circulates through radiators to enhance heat dissipation.
Step 7
State the function of the Buchholz relay in a transformer.
96%
114 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The Buchholz relay monitors the gas formation inside the oil of a transformer. It serves to sound an alarm when gas is formed, isolate the transformer when gas exceeds a certain level, and protect the transformer from damage.
Step 8
Calculate the:
5.8.1 Primary line current
99%
104 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
To calculate the primary line current (IL1):
IL1=3VL1S=3⋅11kV100kVA≈5.25A
Step 9
Calculate the:
5.8.2 Secondary phase voltage
96%
101 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
To determine the secondary phase voltage (VPH2):
Using the transformer ratio:
N2N1=VPH2VPH1
Calculating:
VPH2=NRVL1=4811kV≈229.17V
Step 10
Calculate the:
5.8.3 Active (true) power
98%
120 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The active (true) power (P) can be calculated as:
P=S⋅pf=100000⋅0.9=90kW
Step 11
Draw a diagrammatic representation of the transformer coils.
97%
117 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Here is a simple diagrammatic representation of the transformer coils:
L1 L1 L2 L2 L3 L3
|------| |------| |------|
| | | | | |
N N N N N N
In this representation, the lines indicate connections and the primary coils are denoted accordingly.
Step 12
Explain whether it is a step-down or step-up transformer.
97%
121 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
This is a step-down transformer because the winding ratio is 48:1, meaning the primary voltage is higher than the secondary voltage.
Step 13
Explain, with a reason, the relationship between voltage and current of a step-down transformer.
96%
114 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
In a step-down transformer, the voltage is reduced while the current is increased to maintain power conservation. This is a consequence of the transformer equation, where the power input equals the power output, leading to the relationship:
Pin=Pout⇒VinIin=VoutIout